- Wisconsin
- PE (Retired) - Power Systems
mull982 said:Will the breaker trip if the continuous current reaches a level of 35 or 40A? What will cause the breaker to trip in this case since it is an instantaneous breaker?
No the breaker will not trip, but it will probably eventually fail due to overheating. As I said earlier think of its continuous rating like it was a piece of wire not like a trip rating. The breaker trips instantly when it reaches its set point (which is a multiple of its continuous rating).
Typical small "MCP" breakers continuous current ratings are 3, 7, 15, and 30A with 300-1100% trip settings.