nawao
- Abuja - Nigeria
If one phase of the high legs on a delta is missing, what will be the 120/208 relationship on a wye bank
Yes, this is exactly what I'm asking forAre you asking what the wye secondary voltages would be if the delta primary lost 1 phase?
Yes, this is exactly what I'm asking forjim dungar said:Are you asking what the wye secondary voltages would be if the delta primary lost 1 phas
If one of the primary lines opens, you are left with a single phase system. If we lost Vb for example,Yes, this is exactly what I'm asking for
My earlier statement would be more accurate if it were stated, "If you lost 1 of the primary lines, 2 lines of the secondary will have reduced voltage and no longer have a 120? out-of-phase relationship."If you lost 1 line on the primary you will lose 2 lines on the secondary.
I agree with your phasing assessment. However, I believe it would be less than 104V, because the two primary windings would be operating at half voltage. Say on a 480 Delta to 208Y/120 xfmr, the primary windings typically fed by the lost line would normally have 480V across each. With that line missing, they would have 480V across both in series, thus 240V across each. That figures out to 60V to Neutral output on the affected secondary windings.If one of the primary lines opens, you are left with a single phase system. If we lost Vb for example,
Van = 120V @ phi
Vbn = Vcn = 104V @ phi +/- 180
This occurs because two of the primaries are now in series, driven by Vac.
I know the feeling :grin:Oh I hate to be wrong! Worse yet, I hate to admit being wrong!
Hmmm... Hate to say it, but wouldn't line-to-line secondary voltages be 180, 120, and 60? That is, Van = 120V, then + and – 60V for the two other affect windings.And, Vbc = 0
Van = 120V @ phi
Hmmm... Hate to say it, but wouldn't line-to-line secondary voltages be 180, 120, and 60? That is, Van = 120V, then + and ? 60V for the two other affect windings.
Vab = Van + Vnb = 120 + -60 = 60V
Vbc = Vbn + Vnc = 60 + 60 = 120V
Vac = Van + Vnc = 120 + 60 = 180V
How did you calculate Vbn = Vcn = 104V @ phi +/- 180?
Look carefully at the polarity dots. Both Vbn and Vcn are 180 out from Van.
OK... my turn to say I was wrong
Vab = Van + Vnb = 120 + 60 = 180V
Vbc = Vbn + Vnc = -60 + 60 = 0V