Phase missing

Status
Not open for further replies.
If one phase of the high legs on a delta is missing, what will be the 120/208 relationship on a wye bank

What system are you speaking of? A high-leg delta, or a wye?

If a phase is out on a wye, you still have two 120 volt and one 208 volt connections.

If high-leg delta, which phase?

Is the delta a transformer primary to the wye?
 
Are you asking what the wye secondary voltages would be if the delta primary lost 1 phase? Or, are you asking what they would be if you lost one of the delta primary windings, but keep all 3-phases?
 
jim dungar said:
Are you asking what the wye secondary voltages would be if the delta primary lost 1 phas
Yes, this is exactly what I'm asking for

1 line or 1 winding?

If you lost 1 line on the primary you will lose 2 lines on the secondary.

If you lost 1 winding on the primary, you will lose 1 line on the secondary
 
Yes, this is exactly what I'm asking for
If one of the primary lines opens, you are left with a single phase system. If we lost Vb for example,

Van = 120V @ phi

Vbn = Vcn = 104V @ phi +/- 180

This occurs because two of the primaries are now in series, driven by Vac.
 
Last edited:
If you lost 1 line on the primary you will lose 2 lines on the secondary.
My earlier statement would be more accurate if it were stated, "If you lost 1 of the primary lines, 2 lines of the secondary will have reduced voltage and no longer have a 120? out-of-phase relationship."

If one of the primary lines opens, you are left with a single phase system. If we lost Vb for example,

Van = 120V @ phi

Vbn = Vcn = 104V @ phi +/- 180

This occurs because two of the primaries are now in series, driven by Vac.
I agree with your phasing assessment. However, I believe it would be less than 104V, because the two primary windings would be operating at half voltage. Say on a 480 Delta to 208Y/120 xfmr, the primary windings typically fed by the lost line would normally have 480V across each. With that line missing, they would have 480V across both in series, thus 240V across each. That figures out to 60V to Neutral output on the affected secondary windings.
 
Yer Right!

Yer Right!

My earlier statement would be more accurate if it were stated, "If you lost 1 of the primary lines, 2 lines of the secondary will have reduced voltage and no longer have a 120? out-of-phase relationship."


I agree with your phasing assessment. However, I believe it would be less than 104V, because the two primary windings would be operating at half voltage. Say on a 480 Delta to 208Y/120 xfmr, the primary windings typically fed by the lost line would normally have 480V across each. With that line missing, they would have 480V across both in series, thus 240V across each. That figures out to 60V to Neutral output on the affected secondary windings.

Oh I hate to be wrong! Worse yet, I hate to admit being wrong!

And, Vbc = 0
 
Oh I hate to be wrong! Worse yet, I hate to admit being wrong!
I know the feeling :grin:

And, Vbc = 0
Hmmm... Hate to say it, but wouldn't line-to-line secondary voltages be 180, 120, and 60? That is, Van = 120V, then + and – 60V for the two other affect windings.

Vab = Van + Vnb = 120 + -60 = 60V
Vbc = Vbn + Vnc = 60 + 60 = 120V
Vac = Van + Vnc = 120 + 60 = 180V
 
Last edited:
If one of the primary lines opens, you are left with a single phase system. If we lost Vb for example,

Van = 120V @ phi

Vbn = Vcn = 104V @ phi +/- 180

This occurs because two of the primaries are now in series, driven by Vac.

How did you calculate Vbn = Vcn = 104V @ phi +/- 180?
 
Not quite:

Not quite:

I know the feeling :grin:


Hmmm... Hate to say it, but wouldn't line-to-line secondary voltages be 180, 120, and 60? That is, Van = 120V, then + and ? 60V for the two other affect windings.

Vab = Van + Vnb = 120 + -60 = 60V
Vbc = Vbn + Vnc = 60 + 60 = 120V
Vac = Van + Vnc = 120 + 60 = 180V

Look carefully at the polarity dots. Both Vbn and Vcn are 180 out from Van.
 
Mistake:

Mistake:

How did you calculate Vbn = Vcn = 104V @ phi +/- 180?

As Smart pointed out, these voltages should be 60V because their primaries are in series with a single phase voltage applied. The phase angles are determined by inspection of the primary and secondary polarity dots.
 