Phase Rolling vs Phase swaping
mbrooke
Batteries Included
United States
Technician
Brain freeze- can rolling phases result in reverse spinning or will it go unnoticed? Think ABC gets connected BCA or CAB
FYI I have never heard the term "phase rolling" it must be a regional jargon thing. I remember this thread from a while back someone asked what "bumping phases" meant and I think most hadn't heard that term either.
Actually, I've done this a few times with temp setups; with spider boxes and the like, it always seems like C has the lightest load, then B, so I'll roll the phases from one area forward (ABC-> BCA) and from another area back (ABC-> CAB) to get a better balance. Seems to work (in my environments, mostly single-phase loads).
Its done on distribution circuits. Picture lots and lots of high legs, where one can is always more loaded then the other one or two. By rotating each bank down line you get a nice balance.
On about getting my mind around this one. Suppose you had a 240V 3 PH high leg service on a commercial property with a bunch of heavily loaded Air Conditioning units, and noticed that there was quite a good voltage imbalance seen at the line side of all the RTU disconnects. Could phase rolling be used in this instance and where would you implement it? We are assuming that the way the panel loads were configured, was unbalanced by possibly more single phase loads than what the space originally had.
If you rotate all of them, you just rotated the imbalance.
You should be alternating which line single phase services connect to also, and when an unbalance condition seems to be persistent you change a select few to balance things out. Those high leg delta services need to have "rolling" of primary or swap the non high leg secondary conductors if your balancing act will change rotation.
Presumably, it would be implemented by the utility "rolling" the primary connections to the transformers, to reduce a voltage and/or current imbalance in the primary-voltage distribution phases.