- Location
- Wisconsin
- Occupation
- PE (Retired) - Power Systems
It is important for paralleled power sources like with closed transition transfer switches.What difference would it make? Only the rotation is important.
It is important for paralleled power sources like with closed transition transfer switches.What difference would it make? Only the rotation is important.
Well those situations are kind of important to actually be "in phase" with one another, even if only dealing with single phase supply.It is important for paralleled power sources like with closed transition transfer switches.
?Where I worked we always had clockwise rotation. Rolled the motor leads if rotation was wrong
For a new service, we worked with POCO to get CW
Yep, saw a plant lose utility power when a transfer switch on the utility side stuck and the phases didn't match, although rotation was the same.Well those situations are kind of important to actually be "in phase" with one another, even if only dealing with single phase supply.
It is only important that they agree on which is the A phase and the direction of rotation, not that any phase is absolutely the A phase.It is important for paralleled power sources like with closed transition transfer switches.
until you run into high leg or corner grounded delta systems.It is only important that they agree on which is the A phase and the direction of rotation, not that any phase is absolutely the A phase.
You are correct that there is no absolute 'A phase'. Paralleled sources, including utility grids, need to have a common reference phase and rotation.It is only important that they agree on which is the A phase and the direction of rotation, not that any phase is absolutely the A phase.
Or Natural Grey (whatever that is)?There is no code on which colors to use however the standard for 3 phase 120/208 is black, red, blue. In your case you would have to mark the white conductor with any color other than white or green.
Whatever the color scheme in the building is then you should follow it when there are other voltages like 277/480
pretty certain more recent code editions have eliminated "natural grey" wording and just go with white or gray for the required grounded conductor color requirements now.Or Natural Grey (whatever that is)?
I was just saying that White, Grey, Green and Orange are the special colors.pretty certain more recent code editions have eliminated "natural grey" wording and just go with white or gray for the required grounded conductor color requirements now.
I think the natural grey was the color that came out when not adding any specific coloring pigments when making the insulation?
Now it is, but 20* or so years ago it wasn't. Instead of gray, it (NEC) mentioned natural.I was just saying that White, Grey, Green and Orange are the special colors.
While not a new service, it can be a huge issue on an existing service where the utility flops the rotation.?
For a new service you get what we deliver. Up to you to roll motor leads to make them turn like you want.
Why would it matter CW or CCW at the service point?a
Agreed. We are meticulous when it comes to existing services and rotation when we do any workWhile not a new service, it can be a huge issue on an existing service where the utility flops the rotation.
A number of years ago, a contractor working for the local utility replacing some medium voltage lines and transformers, reversed the rotation on the supply to one of the city's deep wells. It was a shaft driven submerged deep well pump. The backwards rotation spun the shaft apart requiring a costly fishing project to recover the pump and restore it to service.
Of course, but in those cases it's easy to tell what's what with a voltmeter.until you run into high leg or corner grounded delta systems.
I've seen a few line shaft turbines pumps with the headshaft sticking up up thru the roof after accidently being run in the wrong direction. We usually install a non-reverse rachet on the motor, or a backspin timer. The backspin timer allows the pump to stop backspinning caused by the column pipe draining.While not a new service, it can be a huge issue on an existing service where the utility flops the rotation.
A number of years ago, a contractor working for the local utility replacing some medium voltage lines and transformers, reversed the rotation on the supply to one of the city's deep wells. It was a shaft driven submerged deep well pump. The backwards rotation spun the shaft apart requiring a costly fishing project to recover the pump and restore it to service.
Ya but you guys have the hot water on the right, cold on the left, and light switches are down for on.For many years UK 3-phase colours were red, yellow, and blue. Primary colours. Now we have this nonsense:
For three-phase cables the phase colours are brown, black and grey, instead of red, yellow and blue, respectively, and the neutral colour is now blue instead of black. Again the protective conductor is identified by the colour combination green-and-yellow.