A real head-scratcher:
We cutover a feeder to a new breaker serving a 300 KVA xfmr. The original breaker was a 600A but the engineers downsized the new breaker to a 400A after reviewing the metering and realizing the load was very low. When we reenergized the xfmr from its new source we found rotation was backwards. We then swapped rotation and tried closing the breaker but it tripped instantly.
Thinking we may have shorted a wire or crossed phasing, we took apart our wiring and tested everything. All was good until we landed the wires back on the primary and tried to reenergize again. The breaker still tripped instantly. So we put the rotation back to the original way we had it (counter-clockwise) and the breaker would hold?? No one could explain it. I went back to the new breaker and turned the instantaneous setting all the way up and this time the breaker would hold with the correct rotation. What I don't understand is why the breaker would hold with counter-clockwise rotation, but trip with clockwise rotation before adjusting the instantaneous trip setting? There was no load on the secondary side of the xmfr either. Would the inrush from the transformer change based on rotation?
We cutover a feeder to a new breaker serving a 300 KVA xfmr. The original breaker was a 600A but the engineers downsized the new breaker to a 400A after reviewing the metering and realizing the load was very low. When we reenergized the xfmr from its new source we found rotation was backwards. We then swapped rotation and tried closing the breaker but it tripped instantly.
Thinking we may have shorted a wire or crossed phasing, we took apart our wiring and tested everything. All was good until we landed the wires back on the primary and tried to reenergize again. The breaker still tripped instantly. So we put the rotation back to the original way we had it (counter-clockwise) and the breaker would hold?? No one could explain it. I went back to the new breaker and turned the instantaneous setting all the way up and this time the breaker would hold with the correct rotation. What I don't understand is why the breaker would hold with counter-clockwise rotation, but trip with clockwise rotation before adjusting the instantaneous trip setting? There was no load on the secondary side of the xmfr either. Would the inrush from the transformer change based on rotation?