I take the portion I bolded to mean there was a factory link or jumper from B phase to the transformer case/housing. If so that is an intentional bond to create a corner grounded system and the voltage readings you posted are exactly what should be expected.Hi to All!
I apologize for taking to long to respond.
I've conducted test at loadside of the xfrmr, as you have suggested, and here are the results:
Vab = 240V
Vbc = 240V
Vca = 240V
Vag = 240V
Vbg = 0V
Vcg = 240V
Connection wiring of 500kVA, 480V/240V Dry Type Xfrmr: Delta (P) and Ungrounded Wye (S)
We then traced the connections of the secondary, we found that phase B was body grounded. Is this what may have caused grounding of Phase B? Or are there external factors that contributes to this grounded phase?
We tried disconnecting the panel where we found a grounded phase B, and readings were back to normal (expected readings). Then tried to connect it again, at first all is well but after a couple of minutes, phase B was again grounded.
Also, yes we patterned our code to the NEC with certain ammendments.
I am a little confused at what you intend to mean with this "Connection wiring of 500kVA, 480V/240V Dry Type Xfrmr: Delta (P) and Ungrounded Wye (S)" Though you apparently don't exactly follow NEC. In general there is no such thing as an ungrounded wye system if you are using NEC. I also not sure if 480 is primary or secondary voltage though it seems it likely is primary voltage, or what is wye and what is delta, or if there even is a wye side to the transformer. Sounds like whichever side you are measuring is a 240 volt corner grounded system though.
So what I am seeing so far is that you do have a corner grounded delta supply, you just apparently haven't seen one before and don't fully understand what you have or how to work with it. You can supply 240 volt loads (single or three phase) with it. One conductor happens to be grounded, but is still the same potential to the other conductors of the system and the load(s) only care about receiving proper voltage and could care less which conductor is grounded. (get into some electronics and digital signaling circuits and this gets more complicated but a simple three phase motor or resistive load won't care what is grounded or what isn't) There is no 120 volt taps to this system, if you need 120 volts for something you will need to separately derive it.