K kchartwig New member Apr 8, 2010 #1 With a primary distribution voltage of 13.2 kv how do I find the phase to ground voltage for a grounded wye or delta. thanks
With a primary distribution voltage of 13.2 kv how do I find the phase to ground voltage for a grounded wye or delta. thanks
zog Senior Member Location Charlotte, NC Apr 8, 2010 #2 kchartwig said: With a primary distribution voltage of 13.2 kv how do I find the phase to ground voltage for a grounded wye or delta. thanks Click to expand... Wye, divide by 1.732, delta there is no real phase to ground voltage it is floating and depends on the properties of the system.
kchartwig said: With a primary distribution voltage of 13.2 kv how do I find the phase to ground voltage for a grounded wye or delta. thanks Click to expand... Wye, divide by 1.732, delta there is no real phase to ground voltage it is floating and depends on the properties of the system.