Phase Voltage to Ground Differences

Status
Not open for further replies.

Leo1

Member
Location
Los Alamos, NM
What if the most likely reason phase voltage on a 120/240VAC, single family dwelling differs between phases to the equipment ground. Each phase to neutral is approx. 118 volts. However, on phase A to equipment ground is approx. 147 volts and phase B to equipment ground is approx. 72 volts.
 
Sounds like a poorly connected or missing main bonding jumper.
Maybe even more likely a bad neutral connection in the service conductor somewhere. I'd expect more equal voltage most cases where main bonding jumper is missing, and there are no ground faults.
 
Maybe even more likely a bad neutral connection in the service conductor somewhere. I'd expect more equal voltage most cases where main bonding jumper is missing, and there are no ground faults.

The phase to neutral voltage is approximately the same I would expect a bad neutral to have a wider difference. The connection to the EGC (where he has the problem phase to EGC) is with the MBJ.
 
The phase to neutral voltage is approximately the same I would expect a bad neutral to have a wider difference. The connection to the EGC (where he has the problem phase to EGC) is with the MBJ.
Somehow I missed him stating phase to neutral voltage:blink: I almost asked what phase to neutral was.

I agree most likely looking at open circuit in EGC or main bonding jumper, as well as isolation from other grounded objects.
 