iwire said:800.50(B) only applies to the conductors described in 800.50(A) 'running from the last outdoor support to the primary protector'
Once past the protector 800.50(B) is a moot point.
It sounds so much nicer when you say it.
iwire said:800.50(B) only applies to the conductors described in 800.50(A) 'running from the last outdoor support to the primary protector'
Once past the protector 800.50(B) is a moot point.
buckofdurham said:Thank You................
iwire said:No problem. :smile:
I have an idea you may have been looking for 800.133.
My dyslexia did that too when reading the title of the thread....acrwc10 said:In defense of all who think that there should be a separation of church and state, I mean phone lines and line voltage cable.
And there are exceptions - but often people look for this 2" separation....800-52A(2) Other Applications. Communications wires and cables shall be separated at least 50 mm (2 in.) from conductors of any electric light, power, Class 1, non?power-limited fire alarm, or medium power network-powered broadband communications circuits.
iwire said:Not sure what your saying, maybe we are saying the same thing.![]()
The code allows mixing with cables, not with conductors. The code does not care about the interference, the code only cares we don't energize a data cable with line voltage.
Personally I try to keep them apart.
acrwc10 said:In defense of all who think that there should be a separation of church and state, I mean phone lines and line voltage cable.