This should answer your question
This should answer your question
Article 800.133 of the 2008 NEC basically gives you the spacing and your answer. Hope this helps...
800.133 Installation of Communications Wires, Cables,
and Equipment. Communications wires and cables from
the protector to the equipment or, where no protector is
required, communications wires and cables attached to the
outside or inside of the building shall comply with
800.133(A) through (C).
(A) Separation from Other Conductors.
(1) In Raceways, Cable Trays, Boxes, and Cables.
(a) Other Power-Limited Circuits. Communications
cables shall be permitted in the same raceway, cable tray, or
enclosure with cables of any of the following:
(1) Class 2 and Class 3 remote-control, signaling, and
power-limited circuits in compliance with Article 725
(2) Power-limited fire alarm systems in compliance with
Article 760
(3) Nonconductive and conductive optical fiber cables in
compliance with Article 770
(4) Community antenna television and radio distribution
systems in compliance with Article 820
(5) Low-power network-powered broadband communications
circuits in compliance with Article 830