Mark
Mark
busman said:I guess I'm going to have to stop putting single-pole contactors on A/C units (not).
Mark
busman said:I guess I'm going to have to stop putting single-pole contactors on A/C units (not).
Mark
480sparky said:Why? If you're using it as a controller, that's fine.
iwire said:No, not fine.
410.54 is not just for disconnecting means, it is about the 'switching means'
480sparky said:But for what, exactly, does that section apply to? Certainly not AC units.
480sparky said:It will work, but it's a bad design, since you're only turning off one of the ungrounded conductors. Some poor, uneducated and unlicened maintainence man could get zapped if the photocell shut them off, but the power was still on.
480sparky said:So how does that apply to post 21?
chevyx92 said:Had a co-worker ask me this this morning and I couldn't come up with the answer. If you have some 208v volt wall packs and want to use a photocell to control them why can't you use a 120v photocell? Why does it HAVE to be rated 208v when all you are doing is breaking one leg of the 208.
480sparky said:But for what, exactly, does that section apply to? Certainly not AC units.
growler said:Back to the original question. A 120 V photocell used to control 208 V lighting.
Answer: Use photo cell to control 120 V coil of two pole lighting contactor. End of story.![]()
chevyx92 said:. If you have some 208v volt wall packs and want to use a photocell to control them why can't you use a 120v photocell?
peter d said:just say that the reason you can't use a 120 volt photocell is because the code doesn't allow it.
tom baker said:Its very common to only break one leg
tom baker said:Its very common to only break one leg of a 208 or 240 volt luminaire. Many photocells are multivoltage rated, IE 120-208 120-240.