This is one of those weird things in the NEC where they just never bothered to make a distinction. You can have a bare EGC or an insulated EGC. If it's insulated the voltage rating of the insulation needs to match or exceed the highest voltage in the other conductors. Yes, it makes no sense, but that's how it's written. This question comes up fairly regularly and maybe your AHJ won't care, maybe they will. If they won't allow it there is no code substantiation you can use to justify the lower rating of the EGC insulation.
Based on what I hear, almost no AHJs care about this. But there's always that one AHJ hiding out there who does not say anything until the final inspection, and then they get you.
Based on what I hear, almost no AHJs care about this. But there's always that one AHJ hiding out there who does not say anything until the final inspection, and then they get you.