wwhitney
- Berkeley, CA
- Retired
Today's first PI is to clarify that you can put a cable in a conduit system that runs to an Article 312 enclosure without securing the cable to the enclosure.
Cheers, Wayne
(C) Cables.
Where a cable wiring method is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.
Statement of Problem and Substantiation for Public Input
The current wording appears to cover cables that enter a cabinet through a complete raceway system from another enclosure. However I do not believe that is the intent; the analogous section for junction boxes, 314.17(B), exempts that case in subsection (3). The proposed revision clarifies that the requirement does not apply to raceway wiring methods.
Cheers, Wayne
(C) Cables.