Check the last line of 314.17(B).
Lou
Lou
Check the last line of 314.17(B).
Lou
I'm not installing it, I'm passing through it.:smile:314.17(B) Metal Boxes and Conduit Bodies. Where metal boxes or conduit bodies are installed with messenger-supported wiring, open wiring on insulators, or concealed knob-and-tube wiring, conductors shall enter through insulating bushings or, in dry locations, through flexible tubing extending from the last insulating support to not less than 6 mm (? in.) inside the box and beyond any cable clamps. Except as provided in 300.15(C), the wiring shall be firmly secured to the box or conduit body. Where raceway or cable is installed with metal boxes or conduit bodies, the raceway or cable shall be secured to such boxes and conduit bodies.
I have to agree with you, I can't see why someone would do if they planed the job right.
Lou
I have to agree with you, I can't see why someone would do if they planed the job right.
Lou