Pipe in pull box

Status
Not open for further replies.
Check the last line of 314.17(B).
Lou

I would argue that all day long.


314.17(B) Metal Boxes and Conduit Bodies. Where metal boxes or conduit bodies are installed with messenger-supported wiring, open wiring on insulators, or concealed knob-and-tube wiring, conductors shall enter through insulating bushings or, in dry locations, through flexible tubing extending from the last insulating support to not less than 6 mm (? in.) inside the box and beyond any cable clamps. Except as provided in 300.15(C), the wiring shall be firmly secured to the box or conduit body. Where raceway or cable is installed with metal boxes or conduit bodies, the raceway or cable shall be secured to such boxes and conduit bodies.
I'm not installing it, I'm passing through it.:smile:
 
I don't think 314.17(B) is applicable.

Maybe it's code compliant, but I still think the stuff shown in the pictures is stupid.:smile:
 