pulliteasy
Member
Hi again fella's
Got a question about the right and wrong in a place of assembly. Ok, the company I work for just built a 40'x 60' addition onto a church which will be used as a fellowship hall.There is a new kitchen,2 bathrooms several closets and a couple of offices and a large open area for tables or just what ever. There will be fire guard sheet rock in this addition as well. For the majority of the church the wiring is in conduit,however there is a added plug here and there that just has romex ran to it. The company license holder is planning on running all the wiring for this addition in romex. From what I have read in the code book this is a no no. I am not positive on the 100 people part but feel sure it will hold that many in the church. Please give me some code and why this is not good, or tell me it is ok? thanx again for your replies.
Got a question about the right and wrong in a place of assembly. Ok, the company I work for just built a 40'x 60' addition onto a church which will be used as a fellowship hall.There is a new kitchen,2 bathrooms several closets and a couple of offices and a large open area for tables or just what ever. There will be fire guard sheet rock in this addition as well. For the majority of the church the wiring is in conduit,however there is a added plug here and there that just has romex ran to it. The company license holder is planning on running all the wiring for this addition in romex. From what I have read in the code book this is a no no. I am not positive on the 100 people part but feel sure it will hold that many in the church. Please give me some code and why this is not good, or tell me it is ok? thanx again for your replies.