brycenesbitt
Senior Member
- Location
- United States
I have a plan checker who has approved our project except that they want a listing showing that the Eaton FAZ series breakers we selected are compatible with the EK012-012 enclosure that's part of the assembly. The issue is NOT the top level listing, the issue is the component listing between the breaker and the DIN rail enclosure.
The enclosure vendor wrote:
But the plan checker is not satisfied. The EK panel board is listed under BGUZ.E254144 by Guenther Spelsberg GmbH + Co. KG.
---
The plan checker wants a document from Eaton saying that this breaker is compatible with this enclosure.
And they want specific written proof in UL50, IEC 61439, or IEC 62208 document (highlighted in yellow)
that breakers can be interchanged between different vendor enclosures.
The written plan check correction is:
The checker (and his boss and his boss) wants Eaton to say that the Eaton product can go into the Guenther Spelsberg enclosure..
I have not been able to get Eaton to agree to write a letter to that effect.
The AHJ refuses to call the vendors, or check product IQ.
Thoughts on strategy?
Nobody is claiming an electrical problem. Everything else checks out. It's just a paperwork issue. 508 is not involved that's not the issue. The issue is component listing between the breaker and the DIN rail enclosure.
The enclosure vendor wrote:
This email is to confirm that our EK012 series enclosure part number 542-512 is UL listed under UL file number E254144.
These standards for this type of enclosure do not limit what specific electrical products can be installed in the enclosure.
Any UL approved DIN rail mount breaker, like the Eaton FAZ series or similar breakers, can be installed in this enclosure without any issues.
But the plan checker is not satisfied. The EK panel board is listed under BGUZ.E254144 by Guenther Spelsberg GmbH + Co. KG.
---
The plan checker wants a document from Eaton saying that this breaker is compatible with this enclosure.
And they want specific written proof in UL50, IEC 61439, or IEC 62208 document (highlighted in yellow)
that breakers can be interchanged between different vendor enclosures.
The written plan check correction is:
The panel board shape is willing to say Eaton is OK. But the plan checker will not consider their input.Electrical 1 PC2:
Circuit breakers must be listed for the specific panelboard they go into, as
confirmed by the manufacturer. Please provide documentation showing the Altech [EK012]
enclosure is listed for different installations. [CEC 110.3(B)]
The checker (and his boss and his boss) wants Eaton to say that the Eaton product can go into the Guenther Spelsberg enclosure..
I have not been able to get Eaton to agree to write a letter to that effect.
The AHJ refuses to call the vendors, or check product IQ.
Thoughts on strategy?
Nobody is claiming an electrical problem. Everything else checks out. It's just a paperwork issue. 508 is not involved that's not the issue. The issue is component listing between the breaker and the DIN rail enclosure.
Last edited: