I would sometimes, not say always, this should be spelled out in clear terms in the contract documents.Originally posted by dduffee260:
I have always been informed that specs override plans.
this doesnt sound right, so your saying pick the most expensive method between the two?Originally posted by iwire:
If the specs say 12 AWG but the prints say 10 AWG you have to use 10 AWG.
If the specs say receptacles shall be placed every 6' but the plans show 12' you must place them at 6'.
In general the contractor does not get to choose the paper that that is easier or less costly to follow.
Yes, that is exactly what I am saying.Originally posted by gmreynol:
this doesn't sound right, so your saying pick the most expensive method between the two?
There is no contract when you are bidding a job, I do agree with the RFI and qualifying, ty for youre inputOriginally posted by jim sutton:
Sorry but there is no such thing as "normal". The contract is what it is. Every job has a different contract and should be read.
As for the NM vs MC issue, you should send in an RFI now or qualify your bid.