Stevenfyeager
- United States, Indiana
- electrical contractor
Is it ok to use plastic zip ties to support MC cable in a commercial building ? Thank you
They have to be rated for cable supportIs it ok to use plastic zip ties to support MC cable in a commercial building ? Thank you
Yes, and there are probably trillions of them holding up MC cable in buildings across the country.
The master has spoken.
I just did it today.
Ran 50' of MC cable down a hall way above a suspended ceiling. There was this gorgeous piece of 1" rigid aluminum conduit heading to the same location. Couldn't resist myself and violated the heck out of 300.11 B
I may be going to hell for that one!
haha. Wouldnt rigid be rated to support cables tho?
300.11
B) Raceways Used as Means of Support. Raceways
shall be used only as a means of support for other raceways,
cables, or nonelectrical equipment under any of the
following conditions:
(1) Where the raceway or means of support is identified for
the purpose
(2) Where the raceway contains power supply conductors
for electrically controlled equipment and is used to support
Class 2 circuit conductors or cables that are solely
for the purpose of connection to the equipment control
circuits
(3) Where the raceway is used to support boxes or conduit
bodies in accordance with 314.23 or to support luminaires
in accordance with 410.36(E)
Honestly, I don't even know where to look to see if 1" rigid aluminum conduit is identified to support 12/3 w/G MC cable. I didn't see anything in Art 344
I'm calling it a gray area![]()
What ever helps you sleep at night!
I'M sure his excellency, "The Master", would never do such a hideous thing. :happyno:
(For other's reference, note he did not capitalize "code"Never, I obey the code 100% of the time.![]()