I have a control panel using an Eaton ELC controller for operation and for alarm outputs. The outputs OPEN on a fault. Recently, there have been some power issues at this location, and we've gotten multiple alarms. I'm thinking the power outage (before a generator kicks in) is opening these outputs, but that seems like a stupid design. Is this at all common?
The Eaton manual says the controller will continue operating with a power loss of 5-10ms, but that's obviously way to quick for a utility-out, generator start, transfer situation. I've added a delay between the output going to alarm and when somebody gets notified, but the whole opening on fault seems crazy except for very certain situations.
The Eaton manual says the controller will continue operating with a power loss of 5-10ms, but that's obviously way to quick for a utility-out, generator start, transfer situation. I've added a delay between the output going to alarm and when somebody gets notified, but the whole opening on fault seems crazy except for very certain situations.