Romex not rated for wet location?
Nope, not even damp, unless it is the elusive NMC type. So the space from the building wall to the box, though small, is outside. So that section and the connector are in violation. Even if enveloped in duct seal or silicone.
If building finish was used to connect the box to the brick (by mortar), one might make a case that the NM assembly does not exist outside of the building. Probably not me, though.