Please confirm my code compliance - wire size with transition.

Status
Not open for further replies.

KaBoom!

Inactive, Email Never Verified
Location
NJ
I have to get a feeder to a new unattached garage. There is an existing 1" PVC pipe going under the patio for me to use. I would like to install as large of a feeder as I can.

My plan is to run #4 aluminum SER from the main panel thru the basement to an outdoor box in which I splice into #6 THWN running thru the 1" PVC.

Both the #4 AL and #6 copper have an allowable ampacity of 65A which means I should be able to use a 70A feeder (assuming that the load is much less than 65A).

Is this all correct?
 
Why can't you use larger conductors in the PVC?
I could squeeze #4’s but I have always upsized underground pipe and I am not sure how many bends the installer put in this run.

I figure 70A will be good, if what I proposed is infact compliant.
 
Both the #4 AL and #6 copper have an allowable ampacity of 65A which means I should be able to use a 70A feeder (assuming that the load is much less than 65A).
Is this all correct?

Since this is less than 100A, 110.14(C)(1)(a) drives you to the 60 deg column unless you can confirm on both ends of the conductors that it is 75 deg terminations.

Ampacity at 60 deg is 55A, so next standard breaker is 60A
 
Since this is less than 100A, 110.14(C)(1)(a) drives you to the 60 deg column unless you can confirm on both ends of the conductors that it is 75 deg terminations.

Ampacity at 60 deg is 55A, so next standard breaker is 60A
75 degrees on both. A 70A CH CH breaker to a 70A Siemens breaker.
 