This is a general question mainly for the inspectors but all comments welcome.
I have been designing DC power plants for the telecom industry for years, and have been aware we play loose and fast with the code in the design. Mostly with de-rating cables such as having as many as 72 500 MCM cables in a cable tray and not de-rating to 310.15 or having space between cables.
I was always under the impression were allowed to do so because we are a utility, designed under engineering supervision, and the areas are only service by qualified personnel. But I always wondered why in some circumstances like telcos that are not a utility and have equipment in public buildings like high-rises ever got away with it.
Well I was speaking with an ole ex-Ma-Bell power engineer who I have a great deal of respect for and who has forgotten more than I will ever know told me I was all wet. He said the reason is after the rectifiers all the cabling is not premise wiring and is considered utilization equipment, therefore the NEC couldn?t say squat about it.
I argued for a moment because I have been busted for it twice; once in King of Prussia and Reston VA. There I had to install multi-layers of cable rack and have 1-inch air-gap spacing, or quadruple the cable count. Wished I had the premise wiring argument under my belt then, I would have played it out in court as the re-do cost over $1M
What do you inspector types think???
I have been designing DC power plants for the telecom industry for years, and have been aware we play loose and fast with the code in the design. Mostly with de-rating cables such as having as many as 72 500 MCM cables in a cable tray and not de-rating to 310.15 or having space between cables.
I was always under the impression were allowed to do so because we are a utility, designed under engineering supervision, and the areas are only service by qualified personnel. But I always wondered why in some circumstances like telcos that are not a utility and have equipment in public buildings like high-rises ever got away with it.
Well I was speaking with an ole ex-Ma-Bell power engineer who I have a great deal of respect for and who has forgotten more than I will ever know told me I was all wet. He said the reason is after the rectifiers all the cabling is not premise wiring and is considered utilization equipment, therefore the NEC couldn?t say squat about it.
I argued for a moment because I have been busted for it twice; once in King of Prussia and Reston VA. There I had to install multi-layers of cable rack and have 1-inch air-gap spacing, or quadruple the cable count. Wished I had the premise wiring argument under my belt then, I would have played it out in court as the re-do cost over $1M
What do you inspector types think???