Re: Please tell me I am not crazy...
Originally posted by marinesgt0411:
Just out of curiousity how did he engineer the transition from wire to box to device
I'm not sure the term 'engineer' is applicable to this installation! At the receptacle end, the 4 stranded conductors were run into a plastic box, the type with twist-off plastic knockouts, no clamp.
I don't remember what, if anything, was used to support the wire coming down the wall.
I didn't look at the breaker panel end of the installation or the run in the attic..
When I spoke to the inspector, I asked him about the rule requiring that a portion of romex sheath extend into the box (basically arguing that individual conductors can't be legal if you have to have a cable sheath visible inside the box), his answer was that rule only applies if using romex.
Then I asked him what he thought the purpose of that rule was, his response was "why do you think it's there?". I said 2 possibilities come to mind, 1) to verify that you are running romex, 2) to protect the conductors where they are clamped at the box. Then he pointed out that some plastic boxes use the twist-off 'clamps' where it's really just a knockout, not a clamp.
-jim-