In a 3 and 4 story town house style dwellings with attached 2 car garage, I have contractors who are being required to install a fire sprinkler system. The contractor has run the the sprinkler pipe in the garages to drop 4 heads in each garage. The original garage ceiling is 12' in height. The builder did not board the garage ceiling at 12'. The panel board is in the garage and all wiring is properly supported throughout the ceiling and walls.
So, the sprinkler heads were required to be dropped 3 feet per fire marshal instructions. So, they dropped the heads and installed a drywall ceiling at 9 feet to meet the heads. The sprinkler system is a wet system, and in our region, the likelyhood of the sprinkler pipe freezing is very high, so the building contractor has the mechanical contractor supply heat from the furnace to the space in between the original 12 foot ceiling and the new 9 foot ceiling. There is no return vent for this space, only a supply air. Is the space above the 9 foot ceiling considered a space being used for environmental air and should the wiring, which is NMC throughout, be changed to meet the requirements of NEC art. 300.22 (2014)?
Would like to hear your opinions on this.
Thank you
So, the sprinkler heads were required to be dropped 3 feet per fire marshal instructions. So, they dropped the heads and installed a drywall ceiling at 9 feet to meet the heads. The sprinkler system is a wet system, and in our region, the likelyhood of the sprinkler pipe freezing is very high, so the building contractor has the mechanical contractor supply heat from the furnace to the space in between the original 12 foot ceiling and the new 9 foot ceiling. There is no return vent for this space, only a supply air. Is the space above the 9 foot ceiling considered a space being used for environmental air and should the wiring, which is NMC throughout, be changed to meet the requirements of NEC art. 300.22 (2014)?
Would like to hear your opinions on this.
Thank you