WMBELEDES

Member
Location
NY, USA
I've worked in extrusion across the globe for over 20 years. I've been told that the extruder die area is "exempt from being a Class 1 Division 1 area. Well now I'm being asked to prove the precedence. Does anyone know of where this exemption started or where I might find it?
 
I've worked in extrusion across the globe for over 20 years. I've been told that the extruder die area is "exempt from being a Class 1 Division 1 area. Well now I'm being asked to prove the precedence. Does anyone know of where this exemption started or where I might find it?

I don't think there is one. is the area around it classified? if so it would appear that it would have to be at least D2.

I have seen only a handful of plastic extrusion machines and I don't recall any were classified as being in a hazardous area. Maybe there is something special about polystyrene.

as a practical matter maybe it is hot enough that it would not do any good to classify that space.
 
Polystyrene Extrusion Dies

Polystyrene Extrusion Dies

Bob,
If I were to use the definition of a C1D1 or D2 500.5(1&2) it might fall under D1 due to rare occurrence where an operator could inject a bubble of gas into the extruder that is released. If I read 500.5(2)(2), "Concentrations are prevented by positive mechanical ventilation". The plant has wall fans with ceiling louvers that replace quite a large volume of air, might this drop the Zone from D1 to D2? How might this be decided? Is there a more detailed article for testing to determine a zone? If so, is this a self test or a test of a certified mature?

Bill
 
Bob,
If I were to use the definition of a C1D1 or D2 500.5(1&2) it might fall under D1 due to rare occurrence where an operator could inject a bubble of gas into the extruder that is released. If I read 500.5(2)(2), "Concentrations are prevented by positive mechanical ventilation". The plant has wall fans with ceiling louvers that replace quite a large volume of air, might this drop the Zone from D1 to D2? How might this be decided? Is there a more detailed article for testing to determine a zone? If so, is this a self test or a test of a certified mature?

Bill

What kind of gas is it? If it is not flammable it would likely not matter.

Part of classifying an area involves judgement and experience. It might be that experience has shown the risk is very low so it does not need to be classified.
 
Polystyrene Extrusion Dies

Polystyrene Extrusion Dies

What kind of gas is it? If it is not flammable it would likely not matter.

Part of classifying an area involves judgement and experience. It might be that experience has shown the risk is very low so it does not need to be classified.

Flammable, butane and pentane. Our experience shows risk is low but an inspector want's more than precedent.

Bill
 
Flammable, butane and pentane. Our experience shows risk is low but an inspector want's more than precedent.

Bill

If you are unable to convince the inspector it might be necessary to hire someone with a PE after his name who has the experience and knowledge to be able to explain why it is that it does not need to be classified.

It seems to me that the machine manufacturer would be a good place to start. I doubt their product liability insurer would let them sell a product like this that their insurer had not vetted first.
 
I've said before and say again, with the exception of installations within the Scopes of Articles 511 to 516, you cannot classify a location from the NEC itself. You must use one of the Referenced Standards in Section 500.4(B), especially Informational Note No.2. In the OP's case none of them speak directly to the mentioned process either. However, NFPA 497 - 2017, Chapter 5 does address the applicable principals and Section 5.6.4 specifically addresses "experience".

BTW unless the presence of flammable gases or vapors happens under "normal" operating conditions, i.e., when everything is operating as designed, Division 1 is inappropriate per the root definition in Section 500.5(B)(1)(1).
 
BTW unless the presence of flammable gases or vapors happens under "normal" operating conditions, i.e., when everything is operating as designed, Division 1 is inappropriate per the root definition in Section 500.5(B)(1)(1).

In post #3 the OP indicated the gas release is rare but seemed to indicate it did happen as part of the regular operation of the equipment, albeit unintentionally caused by operator error.

ETA: The other issue I would think needs to be considered is how much flammable gas could be released and would it actually do any damage if it actually ignited.

Every time someone uses a butane lighter typically a small amount of raw butane is released into the air before the spark ignites the stream of butane. if the amount of butane released is small enough and disperses fast enough there may not be an ignitable concentration of butane.
 
I have a direction.

I have a direction.

I've said before and say again, with the exception of installations within the Scopes of Articles 511 to 516, you cannot classify a location from the NEC itself. You must use one of the Referenced Standards in Section 500.4(B), especially Informational Note No.2. In the OP's case none of them speak directly to the mentioned process either. However, NFPA 497 - 2017, Chapter 5 does address the applicable principals and Section 5.6.4 specifically addresses "experience".

BTW unless the presence of flammable gases or vapors happens under "normal" operating conditions, i.e., when everything is operating as designed, Division 1 is inappropriate per the root definition in Section 500.5(B)(1)(1).

Thank you,
I am consulting our insurer and purchased NFPA 479 for review. This should hopefully resolve the concerns of the inspector.
Bill
 
In post #3 the OP indicated the gas release is rare but seemed to indicate it did happen as part of the regular operation of the equipment, albeit unintentionally caused by operator error.

ETA: The other issue I would think needs to be considered is how much flammable gas could be released and would it actually do any damage if it actually ignited.

Every time someone uses a butane lighter typically a small amount of raw butane is released into the air before the spark ignites the stream of butane. if the amount of butane released is small enough and disperses fast enough there may not be an ignitable concentration of butane.
Actually, I did read it and considered mentioning it in my previous post but decided not to because it muddies the issue. However it's more or less addressed in the "further" definition of Division 1, Section 500.5(B)(1)(2) where the releases are from frequent repair or maintenance operations not incidental misoperation which, BTW, still isn't operating "as designed". Some additional training may be warranted, but not classifying the location Division 1.

I may as well mention Section 500.5(B)(1)(3) too. This is where a faulty operation will cause a simultaneous release and electrical equipment failure which might create an ignition source. This doesn't appear to apply to the OP either.

Quantity of release is indeed another consideration mentioned in NFPA 497, otherwise the whole world would be at least Division 2 if you apply Section 500.5(B)(2)(1) doggedly. The tendency to over-classify is common when the "classifier" hasn't read Section 500.4(B) IN No.1.
 
Ploystyrene Extrusion Die's

Bob,
If I were to use the definition of a C1D1 or D2 500.5(1&2) it might fall under D1 due to rare occurrence where an operator could inject a bubble of gas into the extruder that is released. If I read 500.5(2)(2), "Concentrations are prevented by positive mechanical ventilation". The plant has wall fans with ceiling louvers that replace quite a large volume of air, might this drop the Zone from D1 to D2? How might this be decided? Is there a more detailed article for testing to determine a zone? If so, is this a self test or a test of a certified mature?

Bill

Bill,

If your plant layout representing the equipment markings found on nameplate's coincide with NEC 505.9(C)(2). Below is the Title of the information included.

"Guidelines for the safe use of flammable blowing agents in the production of extruded polystyrene boards (XPS)"


Tag this link:

https://www.giz.de/expertise/downloads/giz2012-en-guidelines-safety-xps.pdf
 
Bill,

If your plant layout representing the equipment markings found on nameplate's coincide with NEC 505.9(C)(2). Below is the Title of the information included.

"Guidelines for the safe use of flammable blowing agents in the production of extruded polystyrene boards (XPS)"


Tag this link:

https://www.giz.de/expertise/downloads/giz2012-en-guidelines-safety-xps.pdf
Do you actually read (or understand) the stuff you google? You're addicted to google, not the NEC. And you still keep misapplying what you find. This paper is a great example of how IEC Zone 1 is often closer to NEC Division 2 than Division 1.
 
Successfully the attempt to put things in perspective 505.9(A)(3) reiertrate exactly what you taught us in this thread pertaining to "owners engineering judgment".

Of course if you do not feel that was the idea then have it your way.
 
Successfully the attempt to put things in perspective 505.9(A)(3) reiertrate exactly what you taught us in this thread pertaining to "owners engineering judgment".

Of course if you do not feel that was the idea then have it your way.

505 has nothing to do with classification according to the class and division system. It is for the zone system which is completely different and requires a PE to sign off on it. and while it is somewhat similar to the IEC zone system, it is not the same.

once again, whatever language you are translating what you are trying to say to english is not making all that much sense.
 
Polysterene Dies

Polysterene Dies

Do you actually read (or understand) the stuff you google? You're addicted to google, not the NEC. And you still keep misapplying what you find. This paper is a great example of how IEC Zone 1 is often closer to NEC Division 2 than Division 1.

Thank you :Anyone with as much experience with this portion of the code to simply dismiss NEC 501.5 and respond in such a manner should just allow an interrogative stated in the code and move on. It is plain to me.
 
Thank you :Anyone with as much experience with this portion of the code to simply dismiss NEC 501.5 and respond in such a manner should just allow an interrogative stated in the code and move on. It is plain to me.
Obviously you don't know how to properly apply Section 501.5 either. It has nothing to do with how to classify a location.

BTW I suggested 501.5 to it's original proposer back in the 2005 NEC.
 
The attempt was to follow any testing to nameplate marking for electrical apparatus and motors for fans might fit either since post #3 had division/ zone wording in his reply for testing.
 
The attempt was to follow any testing to nameplate marking for electrical apparatus and motors for fans might fit either since post #3 had division/ zone wording in his reply for testing.

I think there is another translation error here. When he used the word zone in post #3 he was not referring to the zone classification system. Sometimes English as a second language is tough because context matters. But I am told other languages have idiosyncrasies as well.
 