I am wiring a few woodworking machines. They have a variety of motor sizes and have power cords for ease of mobility. Each machine will have a dedicated breaker and single receptacle. I remember something in the code about a single receptacle's rating needing to match its breaker. For example...a 15A single receptacle is not permitted on a 20A circuit but a 15A duplex or a 20A single is. If I'm sizing my branch circuit conductors to 125% of the FLC and the breakers to 250%, what is the minimum size receptacle permitted? For example, one saw has a 10hp motor. The conductor will be rated for 30A and the breaker will be 60A. Does the receptacle need to be rated for 60A or 30A? I think 30A since the conductors are rated that. Any thoughts?
Also, on that saw there is a note from the manufacturer that says a 30A circuit is recommended but consult your electrician. It has a 10hp motor and a nameplate rating of 24A. Should I go with 24A x 250% = 60A or the 30A?
 
Re: Plug and receptacle for motors

Does the receptacle need to be rated for 60A or 30A? I think 30A since the conductors are rated that. Any thoughts?
A single receptacle can be larger than the branch circuit it is connected to. Look at 210.21(B)(1):


210.21(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
 
Re: Plug and receptacle for motors

210.21 B 1 brings you to 430.81 C 1/3 hp. or less shall be permitted to have a attachment plug and receptacle as a means of control.
 
Re: Plug and receptacle for motors

Look at 430.108(f) you can have a plug on any HP with a HP rated plug and recptical. 1/3 or less in not requierd to have a HP rated plug or appliance or room AC.
 
Re: Plug and receptacle for motors

RUWired... The saw has a 10HP 208V 3ph motor. The nameplate says 24 amps.

So, match the wire with a 30A recept or the breaker with a 60A recept.
210. 21(B) only says "branch circuit".
 
Re: Plug and receptacle for motors

1.) 30 A receptacle
2.) Overcurrent sized per 430.52
3.) Overload sized per Part III of 430
 
Re: Plug and receptacle for motors

benaround... no starters. The machines have on/off switches and some come equipped with SJ cords w/o plug ends, just little crimp terminations. I'm thinking of calling recept manufacturers and talking to the techs.
 
Re: Plug and receptacle for motors

Dose the equipment come with a data plate? Is at a manufactured piece of equipment?
 
Re: Plug and receptacle for motors

Conmgt,bdarnell hit it right with his remarks.Cord and plug is ok as long as motor has thermal protection in the motor.
Rick
 
Re: Plug and receptacle for motors

430.108 (f) say to use a HP rated plug. 10 hp rated plug is 60amp at 240v How do you get around not haveing a cord and a recptical and branch circuit less than 60 amp
 
Re: Plug and receptacle for motors

Wyatt,Your right, looking at Dons hp rated receptacles chart, 60amp device is for 10hp 208 3phase motors.
Rick
 
Re: Plug and receptacle for motors

I think by picking the recptical option to hook up the machines. it forces you to match the recptical and branch circuit. I culd not find in 430 or 670 any thing that give any leway with 210.21(b)1.
 
Re: Plug and receptacle for motors

I culd not find in 430 or 670 any thing that give any leway with 210.21(b)1.
What kind of leeway were you thinking of? 210.21(B)(1) permits the receptacle to be larger than the branch circuit.
 
Re: Plug and receptacle for motors

You are right it says not less than. I miss read so I guess a 60 amp recpt on a 30 branch circuit with a 60 ocpd is fine.
 
Re: Plug and receptacle for motors

conmgt,

The reason I asked about starters is concern for, loss of power and the ability of the motor to start without warning to the operator when the power is restored!

Wheather it is a major power outage or just a c.b. that needs to be reset,not too many people look to turn 'off' something that is not running.

I hope you consider this.

frank
 