MD84
- Stow, Ohio, USA
What would be the impedance of a neon receptacle tester?
I ask because of some troubleshooting I did today. I was disconnecting some equipment so a customer could move a machine. One item was a 120v receptacle. I checked that it was energized with my fluke 87 hi z dmm and read 120v. I turned off the circuit breaker and then checked again. I still had 109v. I thought it was capacitive coupling. This particular branch circuit did come out of a panel in which all the conductors leave in a common 2" conduit. That supported the thought of capacitive coupling. I did not have a low z meter but I did have a plug in tester. I thought it would have a lower impedance then the 87 and perhaps it would not light up.
It did light up and it showed hot and ground reversed. This was with the breaker off. I turned the breaker on and it now showed hot and neutral reversed.
I tried testing with a non contact voltage tester. It lit up on the neutral with the breaker on or off. It lit up on the hot only with the breaker on.
I traced the wires and found no improper terminations. There was one abandoned conductor in the conduit which was un-terminated and insulated. I checked the panel and I am guessing there is no SBJ. This is a SDS 480:208Y. Neutral to all three lines voltage were balanced. All three lines to ground voltage were imbalanced. I think there were two lines with 200v to ground and one with about 0.
I am thinking that with no SBJ the neutral point was elevated above ground. I did not have time to open the transformer. I will check that tomorrow.
Any thoughts on these readings with these instruments? Confirmation of my theory? I will confirm no SBJ and perform bonding tomorrow. I am thinking this will correct the abnormal results.