Plug in solar and GFIs

I think another thing to keep in mind that real PV system is not like a steady power source. No real PIPV will likely produce anywhere near the max inverter power capacity for longer than a short time without throttling. An 800W PIPV inverter will likely only produce 600-700W in a real system during peak season for a duration that is likely much shorter than the continuous use time limit (3 hours?) used for UL compliance rating of wires and receptacles.
 
I think another thing to keep in mind that real PV system is not like a steady power source. No real PIPV will likely produce anywhere near the max inverter power capacity for longer than a short time without throttling. An 800W PIPV inverter will likely only produce 600-700W in a real system during peak season for a duration that is likely much shorter than the continuous use time limit (3 hours?) used for UL compliance rating of wires and receptacles.
I think that is incorrect. An inverter with a sufficiently high DC/AC ratio and optimal panel orientation will typically output at its continuous current rating for several hours on a clear sunny day in summer. That's why the NEC requires the continuous 125% factor for output conductors and OCPDs. It may be that a smaller percentage of PIPV systems will actually do that, due to less than optimal panel orientation or exposure, but it's not something that can be counted on from a branch circuit safety point of view.
 
I think that is incorrect. An inverter with a sufficiently high DC/AC ratio and optimal panel orientation will typically output at its continuous current rating for several hours on a clear sunny day in summer. That's why the NEC requires the continuous 125% factor for output conductors and OCPDs. It may be that a smaller percentage of PIPV systems will actually do that, due to less than optimal panel orientation or exposure, but it's not something that can be counted on from a branch circuit safety point of view.
Sure if the DC/AC ratio and orientation were all optimal then the peak output could be achieved. However, based on my own experience and observations of others (including systems on pvoutput.org) I really see that for most residential systems. I understand ratings compliance can't count on such factors and I was just commenting on the difference between likely reality vs theoretical worst case scenarios.
 
Sure if the DC/AC ratio and orientation were all optimal then the peak output could be achieved. However, based on my own experience and observations of others (including systems on pvoutput.org) I really see that for most residential systems. I understand ratings compliance can't count on such factors and I was just commenting on the difference between likely reality vs theoretical worst case scenarios.
Did you mean "rarely"?
 
Honestly my biggest worry about plug-in solar, especially at scale, is not electrical. It's loose solar panels flying around in windstorms.

(And yes, I'm a bit resentful because of all the engineering we have to provide to get approval for some rooftop solar. But installing to standards should ensure the panels stay on the roof.)
That’s a fair concern. Loose panels in strong winds could definitely become a hazard if they’re not mounted properly. I think the key difference is proper installation and following building standards. When rooftop systems are installed with the right mounting hardware and wind-load calculations, they’re designed to handle pretty extreme weather. So the standards and approvals might feel like a hassle, but they do help make sure everything stays safely in place.
 
That’s a fair concern. Loose panels in strong winds could definitely become a hazard if they’re not mounted properly. I think the key difference is proper installation and following building standards. When rooftop systems are installed with the right mounting hardware and wind-load calculations, they’re designed to handle pretty extreme weather. So the standards and approvals might feel like a hassle, but they do help make sure everything stays safely in place.
The problem is that while rooftop PV module mounting systems are thoroughly engineered, tested, installed by contractors, and sometimes inspected, Joe Bob apartment dweller attaching a module to the outside of his 10th floor apartment balcony railing does not have to meet the same standards and these modules will probably become detached in a wind storm.
 