Plug in solar and GFIs
I was thinking of one being plugged into the first receptacle in a daisy chain, and an overload being plugged into a receptacle downstream of that one. Lots of scenarios like that where you can end up with more current than was intended on the conductors/devices
Anyone have experience or thoughts on this? How about GIF breakers?
There's a whole working group on this issue you can join.
Send me a PM if you're interested in checking that out.
All these topics are active discussion, and there is a lot of regulatory and advocacy work on this topic now. Recent press:
On the GFCI the issue is that some legacy GFCI products measure current with current transformers, and the designers never considered that power might flow backwards through the wires. CT's are directional, and this means negative current perhaps at a 50:1 or whatever ratio flows into the measuring circuit. The claim is that this negative current can fry the GFCI and/or render the
Breaker masking is a greater theoretical concern, which is more tangled.
Millions of these units are in use in Europe where it's been accepted at all levels from the power companies, to regulators to the checkout gal at Ikea.
What if this thing is plugged into a GFCI protected circuit and something requiring GFCI is also on that circuit. Or that it's a source on a circuit that could be overloaded and as far as the circuit breaker is concerned, nothing is overloaded.
That's called "breaker masking" in the world of plug in solar.
GFCI receptacles and likey GFCI circuit breakers in general all have just one CT with all the "protected conductors" passing through it.
If equal current is flowing both ways the voltage produced by the CT coil is zero and the trip function is not initiated. It doesn't know or care which way anything is flowing, all it cares about is that there is not enough imbalance to cause enough CT output to initiate the trip process.
That said any out of phase non-linear currents passing through could cause undesired tripping just like they often do in other situations.
So I kind of doubt the GFCI will care as long as current passing through it is balanced and has fairly low distortion levels
If we look at the UL 943 standard that tests GFCIs we see that they are not tested for operation with a power source plugged into the load side. They are tested for miswiring where a source is wired to the load side and they are supposed to shutdown. So GFCIs are not listed for back feed. I would not plug a power source into a GFCI in my house.
Is any of the traditional outlets (GFCI or not) tested/listed for back feed (i.e. inlet)? It would seem odd if they were as that's contrary to their original intended use case.
The electrons can't tell which direction the receptacle outlet is oriented. Current is current.
A traditional receptacle sees alternating current all the time, both directions. And a 120V receptacle in essence sees power flow both out (for the hot) and in (for the neutral). If you look at receptacle ratings you'll often see the receptacle is rated for a much wider range of voltages and ac/dc current than it's used for.
Breaker masking is a real but unusual edge case.
Current flow direction is an electrical nothingburger with cheese.
I'd bet a milkshake if there are two power sources a utility and small inverter then a cord and plug connected load on the same branch , with one source behind the GFCI and one in front, you would no longer have GFCI protection, as the second source could feed current in to a fault equally with the primary source. Easy experiment would be a plug in one of these inverters to GFCI duplex , replace the PV panel with a regulated DC bench supply to max out the inverter, place a 15k ohm 5 watt ceramic resistor from line to equipment ground on the other receptacle, GFCI wont see the entire load. If a branch circuit has more than one source the alternate source should be plugged into a single receptacle that is not 'down stream' of the GFCI. (Same issue with overload, you'd need a 12 AWG wire and 15A breaker with a max 5A inverter )
The older style receptacles could feed loads side power to their 'slots' even when the line side power had been opened by the GF action or by loss of the .
This issue has been fixed with the latest generation of devices.
The inverter would be grid-tied, and the only N-G bond would be at the service. So if you have a ground fault, current will be flowing through that N-G bond, and that current will show up as a net current through the GFCI CT, regardless of whether that current originated from the utility ungrounded conductor or the inverter ungrounded conductor.
Cheers, Wayne
Cheers, Wayne
I think tortuga chose his resistor example so that the L-N imbalance at the GFCI would be, in his calculation, 4ma on a 8ma fault, and therefore not trip the GFCI on a fault that's supposed to trip it. But he assumes the fault current is divided among the sources, and I'm not convinced this is correct. I think that (almost) the entire fault current would be supplied by the grid tied inverter, if it's capable of backfeeding the receptacle. I believe in that case the fault current travels back to the inverter on the neutral, and trips the GFCI that way. That is, unless there is other load on the circuit that somehow results in some very unlikely equilibrium between the sources at the fault. Which, worse case, doubles the minimum trip current of the GFCI. Unless there's a scenario I've missed.
Maybe I'm missing something, but as I understand it: the service has an N-G bond. The grid tied inverter doesn't. The grid tied inverter is on the load side of a GFCI. We have a high impedance ground fault L-G on the load side of the GFCI.
So there's two possible sources of current through that L-G fault. One is from the service as usual: service L through GFCI through L-G fault through G back to N-G bond on the line side of the GFCI. The GFCI sees this an imbalance, as the current on G does not pass through the GFCI.
The other source of current through the L-G fault is from the inverter. So for that current to return to the inverter N, the path is inverter L through L-G fault through G back to N-G bond on the line side of the GFCI, back through the N through the GFCI to the N at the inverter. The GFCI also see this as an imbalance, as the N current is passing through, but the L current from the inverter is not.
So either way, the GFCI sees the full current through the L-G fault as an imbalance.
Cheers, Wayne
An important point that is worth stating is that these two different sources of imbalance current at the GFCI are additive with each other, rather than potentially cancelling. With the convention that current flows from L to N, the usual balanced case is that the same current travels on L from the line side of the GFCI to the load side, and then travels back on N from the load side to the line side.
But we have utility fault current traveling through the GFCI on L from the line side to the load side plus inverter fault current traveling through the GFCI on N also from the line side to the load side, the opposite of the usual direction on N. That means these two types of imbalance add together as far as the net current through GFCI CT coil.
Cheers, Wayne
Millions of these plug in solar units are in use in Europe.
If there's a problem, it can't be a big one. Sure yes, they don't have neutral to deal with.
But all the other issues exist, and are apparently not a big deal.
I agree that it's unlikely a serious safety issue. I was wondering more from a code/listing perspective.
Cheers, Wayne
I was thinking the current would cancel