alyoshak24
Member
- Location
- Chicago
- Occupation
- Electrician
Hi guys, troubleshooting new construction garage and doing the trim and all outlets and gfi are showing open ground. This is in a garage with main panel not sub panel in garage because they brought service to garage.
Emt all throughout with electrical boxes so emt is being used as grounding system.
Have 3 balanced circuits as follows : A circuit dedicated to all lights, B circuit for car port, C circuit for miscellaneous room
Now the following is what I've done so far. (Used multimeter for all of it...
1. In panel I get 120v from either leg to neutral service conductor.
2. In panel I get 120v from either leg to neutral bus bar
3. In panel I get 50v from either leg to panel frame if I touch black lead tip to panel but if I angle black lead to edge of panel or in holes inside panel the. I get 120v (I didnt have to angle black lead when I touch bus bar or neutral leg)
4. Now outlet in Circuit A carport that has the panel in same room has 1 gfi with 4 other outlets downstream. That gfi is showing open ground but with the multimeter I show 120v from line contractor to EMT pipe. I even ran a ground wire from panel to outlet box and still showing open ground.
5. Even bought ground bar 4 slots and attached 3 grounds to them
6. Panel is grounded to meter via bushing and from meter we have it bonded to to 2 8ft ground rods 6ft apart (however that should not have any influence on a plug in testers reading.
7. Also in circuit A and B (carport / miscellaneous room) when I wiggled tester some outlets and gfis actually showed proper ground and i was able to reset and test gfi with plug in tester reset button...however it was intermittent because when i tried doing it over and over on the outlets and gfis that showed proper ground it then stopped and showed open ground again....again idky but my logic is that if line to pipe or box from a device then bonding is good and so is grounding....
Can you guys please help
Emt all throughout with electrical boxes so emt is being used as grounding system.
Have 3 balanced circuits as follows : A circuit dedicated to all lights, B circuit for car port, C circuit for miscellaneous room
Now the following is what I've done so far. (Used multimeter for all of it...
1. In panel I get 120v from either leg to neutral service conductor.
2. In panel I get 120v from either leg to neutral bus bar
3. In panel I get 50v from either leg to panel frame if I touch black lead tip to panel but if I angle black lead to edge of panel or in holes inside panel the. I get 120v (I didnt have to angle black lead when I touch bus bar or neutral leg)
4. Now outlet in Circuit A carport that has the panel in same room has 1 gfi with 4 other outlets downstream. That gfi is showing open ground but with the multimeter I show 120v from line contractor to EMT pipe. I even ran a ground wire from panel to outlet box and still showing open ground.
5. Even bought ground bar 4 slots and attached 3 grounds to them
6. Panel is grounded to meter via bushing and from meter we have it bonded to to 2 8ft ground rods 6ft apart (however that should not have any influence on a plug in testers reading.
7. Also in circuit A and B (carport / miscellaneous room) when I wiggled tester some outlets and gfis actually showed proper ground and i was able to reset and test gfi with plug in tester reset button...however it was intermittent because when i tried doing it over and over on the outlets and gfis that showed proper ground it then stopped and showed open ground again....again idky but my logic is that if line to pipe or box from a device then bonding is good and so is grounding....
Can you guys please help