what kind of conduit is in my picture?I've seen old installations using black iron piping. Meaning the 1920s.
Well, depends. What does it contain?. Gas, water or wire? Not meaning to be a SA, but black iron was used for different purposes.what kind of conduit is in my picture?
there are wires inside itWell, depends. What does it contain?. Gas, water or wire? Not meaning to be a SA, but black iron was used for different purposes.
Got it, I'm also assuming there is nothing in the code that says you can't use conduit that is not recognized by the NEC?Black iron electrical conduit was a thing a long time ago, but basically people stopped using it post WWII, because galvanizing (as an offshoot of military developments) became too cheap and easy to not just go that route for everything, so conduit suppliers only had to make and inventory one product.
So you can no longer buy black iron electrical conduit now, but you could have in the 1920s and 30s, which is likely what you are looking at here.
As stated black iron RMC the precursor to galvanized RMC. Often call " black pipe".there are wires inside it
The code identifies the acceptable choices in Chapter 300. If it isn't in there, you can't use it for new work.Got it, I'm also assuming there is nothing in the code that says you can't use conduit that is not recognized by the NEC?
Electrical conduit is smooth inside. Plumbing pipe might or might not be.
A lot of things are done that don't meet code. Doesn't mean it won't work, but NEC is there for a reason.I've used galv sch 40 pipe as conduit in a manufacturing plant cause that's all that was on the rack.
344.6 requires that conduit being installed be listed. All of the listed rigid metal conduit is galvanized, so you can't install black enamel protected rigid metal conduit in a new installation.Got it, I'm also assuming there is nothing in the code that says you can't use conduit that is not recognized by the NEC?
(1) Protected from Corrosion Solely by Enamel.
Where protected from corrosion solely by enamel, ferrous metal raceways, cable trays, cablebus, auxiliary gutters, cable armor, boxes, cable sheathing, cabinets, enclosures (other than surrounding fences and walls), elbows, couplings, nipples, fittings, supports, and support hardware shall not be used outdoors or in wet locations as described in 300.6(D).
In a manufacturing plant, who is the AHJ?A lot of things are done that don't meet code. Doesn't mean it won't work, but NEC is there for a reason.
The person handling the money.In a manufacturing plant, who is the AHJ?
Wow….A member posted this years ago. Apparently, it is an operating system of wiring in plumbing PVC. Check out the end caps and how the conduit is reduced.
Be happy you have black iron. lol
View attachment 2571560View attachment 2571561View attachment 2571562View attachment 2571563View attachment 2571564View attachment 2571565View attachment 2571566