Pneumatic Mail - Control Cable

Status
Not open for further replies.

abetovr

Member
Hi,

I believe that many readers know what a Pneumatic Mail System is and how it works, so I'll skip that (unless someone asks).

A local Pneumatic Mail contractor wants to install all the 6" PVC pipes, and then cable-tie-wrap the control cable that travels all along the pipes to the 6" pipe.

1- ?Can the contractor cable-tie-wrap the control cable to the PVC pipe? (I mean, is it NEC allowed?)

2- ?Is there a way I can enforce him (via NEC article) to use a raceway?


-Al
 

iwire

Moderator
Staff member
Location
Massachusetts
The PVC pipe he is installing is not a being used as a raceway so the NEC does not apply to it.

But would you normally allow wiring fasted to plumbing pipes or duct work?
 

abetovr

Member
Pneumatic Mail - Control Cable

Thanks for your answer...

I wouldn't allow either... but I must provide the NEC facts to this contractor...
?may someone give some NEC article numbers where plumbing pipes and like are not allowed as supports?



iwire said:
The PVC pipe he is installing is not a being used as a raceway so the NEC does not apply to it.

But would you normally allow wiring fasted to plumbing pipes or duct work?
 

abetovr

Member
Pneumatic Mail - Control Cable

Well, this is almost the same "problem" I am having!

Answers anyone?


dbuckley said:
Without knowing the answer, would it be acceptable for a central vac system to have its control cable tiewrapped to the vac tube?
 

walkerj

Senior Member
Location
Baton Rouge
As far as the control wiring, the few I have done I ran in conduit to a point designated by the "Pneumatic Mail" guys. We then fished their wires and they terminated.
It seems it would be better off in conduit especially if it's outdoors.
 