Pneumatic Tubing in Electrical Conduit

Status
Not open for further replies.

keithb

New member
I am newly employed in an industry where it is not uncommon to install pneumatic tubing (nylon) inside rigid conduit along with class 1 and/or class 2 wiring. This seems a little strange to me. Can anyone tell me if this allowed by 2002 code?

I would also appreciate help me with a specific code reference regarding the prohibition or permissibility of this practice. Thanks
 
Re: Pneumatic Tubing in Electrical Conduit

Code:
300.8 Installation of Conductors with Other Systems.
 Raceways or cable trays containing electric conductors shall not
 contain any pipe, tube, or equal for steam, water, air, gas,
 drainage, or any service other than electrical.
Don
 
Re: Pneumatic Tubing in Electrical Conduit

This practice is common in prisons. The question came up before, I asked Mike Holt, he seemed to feel 725.3 allowed it with low voltage conductors, but he was not sure.

[ February 08, 2004, 11:01 AM: Message edited by: tom baker ]
 
Re: Pneumatic Tubing in Electrical Conduit

Tom,
It does look like 725.3 would permit this installation as 300.8 is not cited in Artcle 725.
Don
 