Update:
Po co had a bad tap on the primary stop the substation… they changed it out and my transformer went up to the correct voltage.
also had them tap the other transformer we have on site back down because we were getting 502 phase to phase on the three phase side and 253 once we stepped it down with. Idk if 128volts on a regular receptacle would cause harm.
now we have good voltage everywhere 480 with load and 120/240 on the single phase side