Maybe they are giving you a hard time because you are not from the area. It happens.
Definitely a possibility. Although, the POCO manager told me that they've never granted a variance in the 25 years since the policy was implemented.
Maybe they are giving you a hard time because you are not from the area. It happens.
Hard to believe they have such a policy if they serve industrial or agricultural customers whether big or small. If it is just a policy for dwellings I can maybe see it.Definitely a possibility. Although, the POCO manager told me that they've never granted a variance in the 25 years since the policy was implemented.
I'm pretty confused myself. I've never done work in Vermont before and am used to dealing with the POCOs in my area of NY. I know people with 800' driveways who have 4/0s secondaries and have had no problems at all with voltage drop. POCO brought up the issue before connecting and made them sign a waiver releasing them from liability should voltage drop be a problem.
Idle speculation suggests the policy was made because of less-than-qualified persons putting in services with typical sized conductors, likely not even aware of voltage drop considerations. Rather than dealing with problems resulting from such, the POCO implemented the policy.I believe it just applies to dwellings.
Here is one for the utility engineers on this thread.
If I recall in the padmounts there is a primary current limiting fuse that has a minimum interrupting amps and sometimes a optional secondary "breaker" that can be adjusted?
Is there some point at which a bolted L-N fault will not draw enough available fault current to blow the primary current limiter (like a C10) ?
Say they put this service in as they should and size the service lateral as they do with the NESC and lower ambient temp 'k' value. Underground ambient of 20C K=17.3.
2/0 - 2/0 -1/0 AL? 90A load 500 feet one way voltage drop is 5.9% (standard utility stock wire) etc.
Say we have the optional 2.5% taps on the primary and we cant hit one without overvoltaging the closer homes.
So we are delivering 226V at the meter.
If you have a L-N bolted fault on the coldest day of the year 500' away at the meter base and its a 37.5 kva padmount 65C rise with a 1.93%z at 85C with a C10 fuse 2.4kv to ground primary. Or something standard like that.
How long would it take that primary to blow?
Just an update on my situation for you guys...
I met with the POCO's manager and head lineman on Friday and we came to an agreement. They are going to remove the existing transformer and replace it with a junction box. From there, they are going to extend the primary power about 120'-130' and relocate the existing transformer there. I can then set my meter can next to that and go the 250' to my house. All at the cost of about $1,500. I still disagree with having to do it this way, but it ended up costing much less than I had anticipated. I don't have to upsize my wire or conduit now, so I save some money there. In the end, I gave in because I just want to get to work while the weather is nice. But I know I was right.Thanks to everyone for the replies and suggestions.
Sounds like you are lucky just to get them to compromise some. Many POCO get an idea and don't want to change it in that kind of situation.