GerryB
Senior Member
- Location
- woodbridge, ct. USA
Our POCO wants cold sequence for a 400amp 3 phase to a coffee shop. Cold sequence is feed a disconnect, then the meter and on to the panel. We have an outdoor enclosure with a 400 amp breaker which feeds the meter. Then underground 25' to the panel in the coffee shop. 230.82(3) (2014) talks about this (I think) and calls it a "meter disconnect, not service equipment". The question is can that breaker be the service disconnect with all grounding out there and a main lug panel inside? Or should there be a main breaker panel inside the coffee shop. (Also the POCO will be locking access to the breaker outside.) The engineer drawing has a main lug panel inside and all the grounding originating in there, (rods, water, ufer), which definitely doesn't seem right, and just a #3 going out to the main enclosure. Thanks for input.