Point of Attachment

Status
Not open for further replies.

physis

Senior Member
Re: Point of Attachment

Charlie, I like your interpetation, mine is boring and drab. Yours, on the hand, is, interesting, and, thought provoking. :D
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Point of Attachment

Something to consider:

se2.jpg


OR

se1.jpg


If the first figure is correct, then what would we need these for?
230.54 Overhead Service Locations.
(F) Drip Loops. Drip loops shall be formed on individual conductors. To prevent the entrance of moisture, service-entrance conductors shall be connected to the service-drop conductors either (1) below the level of the service head or (2) below the level of the termination of the service-entrance cable sheath.
(G) Arranged That Water Will Not Enter Service Raceway or Equipment. Service-drop conductors and service-entrance conductors shall be arranged so that water will not enter service raceway or equipment.
 

electricmanscott

Senior Member
Location
Boston, MA
Re: Point of Attachment

Twist the words, add parentheses, stop after certain words, spin it anyway you want. I still read it as "Service heads and goosenecks in service entrance cable...." No mention of raceways, although.... Reading from the start of 230.54, (A) requires a service head on a raceway, (B) requires a service head on se cable (exception) allows gooseneck in cable, (C)which has requirements for service heads and goosenecks, seems to tie them all together. Argh! The agony of defeat. :(
 

charlie

Senior Member
Location
Indianapolis
Re: Point of Attachment

I suppose it is too late for me to put in my 2? worth but I'm going to anyway.

It has been our policy to always enforce this section and require the weather head or service head or goose neck to be above the point of attachment. Also, if the point of attachment was right under the eve and ground clearance was close, we would permit the exception to be used and keep the point of contact within 24". If you install service equipment for a service drop in Indianapolis, that is the way it has to be done. :D

Exception: Where it is impracticable to locate the service head above the point of attachment, the service head location shall be permitted not farther than 600 mm (24 in.) from the point of attachment.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: Point of Attachment

Originally posted by iwire: I asked Charlie B to get in on this . . . Now I have to say he was no help at all.
Glad to be of service. ;)

OK. Now I?ve had my morning coffee and have had a chance to read through this discussion again. I still don?t understand it. :confused: But I think that the way physis used parenthesis to clarify the sentence is far more likely than my version to be the intended meaning. That?s one gold star for you physis.
 

captal

Member
Location
MA
Re: Point of Attachment

iwire you were not useless. You made for some very interesting reading on a slow Saturday night.

Al
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Point of Attachment

Guys, you're missing it! It is so much clearer if you read it out loud doing a Walter Kronkite impersonation!

The way it is, the way it was.... :D
 

ronaldrc

Senior Member
Location
Tennessee
Re: Point of Attachment

I guess this is why I'm not very well liked on this site but any plumber will tell you water doesn't flow uphill.

Ronald :)
 

physis

Senior Member
Re: Point of Attachment

Charlie B., I am honored and very grateful to have been nominated for the prestigious and coveted Gold Star award. On behalf of myself and everyone else who has selflessly contributed in the painstaking and arduous task of understanding what is perhaps one of the simplest codes in the NEC.

I must respectfully decline.

All I did was read the code and insert parentheses out of frustration.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Point of Attachment

Originally posted by physis:
I am honored and very grateful to have been nominated for the prestigious and coveted Gold Star award................I must respectfully decline.
Sorry it's already in the mail

star.jpg
 

physis

Senior Member
Re: Point of Attachment

Thanks Bob, my girlfriend just saw that and for her it's a clear confirmation that I am, in reality, a total nerd.
 

russ

Senior Member
Location
Burbank IL
Re: Point of Attachment

Where is the safety issue in this code? I just don't see the common sense of it. I can't think of one wooden riser (6x6 or a temporary service post with a conduit on it) where the attachment point was below the service head. If you have a roof bracket is the service head always required to be above the roof point of attachment? It's common around me to bend a 90 under the soffit and have the service head poke out just beyond the gutter.
I think installing the attachment below the service head is great, but not always reasonable.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: Point of Attachment

Originally posted by iwire: You do know I was just kidding.
I am quite aware you were kidding. So you need not be alarmed about the pair of fully armed nuclear missiles that are current converging on your position. :D
 