roncom0351
- South East Texas
Both the 2005 NEC and the 2007 NESC define the service point as "The point of connection between the facilities of the serving utility and the premises wiring".
I work for a entity that owns our own 138KV Substation with 3 XFMR's reducing down to 12,700 volts. In addition we feed 12.7 to our Central Plant Loop Switch which in turn feeds a 12.7/480 transformer.
My co-inspector and I disagree as to the "service point" he indicates it is before the 138KV substation (as we do not own the line feeding the substation" and I think it is after the 12.7/480 transformer, because if a power meter were installed this is where the CT's would be installed.
Any other thoughts on this matter?