I am bidding a job that has 4 units each with the following:
256 sq ft.
2 small appliance circuits
1 laundry circuit
refrigerator...........1400 watts @ 120 Volts
Dish Washer...........744 watts @ 120 Volts
Microwave............1800 watts @ 120 Volts
Cook top..............7400 watts @ 240 Volts
Wash/Dry Combo...5000 watts @ 240 Volts
Water Heater......27840 watts @ 240 Volts
Electric Heat.........3000 watts @ 240 Volts
According to my calculations the service could be either 206 amps using the standard method for residential calculations or 77 amps using the optional method. This is a huge difference!
My question is this: The water heater can draw 116 amps (it is feed from 2 60 amp 240 volt circuits). If I were to size the service using the optional method I would by code need to use a 100 amp service. If I did the water heater could still draw more than the service could handle. what are the opinions of others on this situation. I feel that the only correct option is to use the standard calculation method but the competition might not. Would it be a violation to use the optional method?
Thoughts please. Thanks
256 sq ft.
2 small appliance circuits
1 laundry circuit
refrigerator...........1400 watts @ 120 Volts
Dish Washer...........744 watts @ 120 Volts
Microwave............1800 watts @ 120 Volts
Cook top..............7400 watts @ 240 Volts
Wash/Dry Combo...5000 watts @ 240 Volts
Water Heater......27840 watts @ 240 Volts
Electric Heat.........3000 watts @ 240 Volts
According to my calculations the service could be either 206 amps using the standard method for residential calculations or 77 amps using the optional method. This is a huge difference!
My question is this: The water heater can draw 116 amps (it is feed from 2 60 amp 240 volt circuits). If I were to size the service using the optional method I would by code need to use a 100 amp service. If I did the water heater could still draw more than the service could handle. what are the opinions of others on this situation. I feel that the only correct option is to use the standard calculation method but the competition might not. Would it be a violation to use the optional method?
Thoughts please. Thanks