memyselfandI
Senior Member
- Location
- Hampton Roads, Virginia
I know that this subject has been beaten to death but I am in a pinch. I was on a job today following behind a crew who just installed 30ft metal direct burial poles on a job. I looked in the hand hole and noticed no EGC connection. I asked them where the EGC was and they said that they did not need to pull one because the pole is metal and in acts as a ground. ??? WTF? I am curious as to find out what code these guys are referring to. I was under the assumption that all non current carrying metal parts of an electrical system must be joined together by a means acceptable to the NEC and that it must be returned to the source where the branch circuit originated from. Am I wrong to assume this? I have to ask them what article they are referring to so I can read it, but if anyone can help me out with this I would greatly appreciate it. I am pressed for time, my son has a Boy Scout meeting here in about 30 minutes and I need to get this potentially dangerous situation taken care of. I found this after the lights were not working and in one of the poles a wire with 277v on it had been cut in the pole hole below grade and it blew the wire apart.The breaker did NOT trip. IMO there is no short circuit protection and this worries me. Any thoughts people?