225.32 Location. The disconnecting means shall be installed
either inside or outside of the building or structure
served or where the conductors pass through the building or
structure. The disconnecting means shall be at a readily
accessible location nearest the point of entrance of the conductors.
For the purposes of this section, the requirements
in 230.6 shall be utilized.
Exception No. 1: For installations under single management,
where documented safe switching procedures are established
and maintained for disconnection, and where the
installation is monitored by qualified individuals, the disconnecting
means shall be permitted to be located elsewhere
on the premises.
Exception No. 2: For buildings or other structures qualifying
under the provisions of Article 685, the disconnecting
means shall be permitted to be located elsewhere on the
premises.
Exception No. 3: For towers or poles used as lighting
standards, the disconnecting means shall be permitted to be
located elsewhere on the premises.
Exception No. 4: For poles or similar structures used only
for support of signs installed in accordance with Article
600, the disconnecting means shall be permitted to be located
elsewhere on the premises.