raider1 said:[quote="clintdenver"
Also a light pole is considered a structure according to article 100 definitions. The exception for a grounding electrode at a light pole is 250.32(A) Exception. This exception says that a structure that is fed with a single branch-circuit that includes an equipment grounding conductor need not have a grounding electrode.
Chris
When you say that this exception is for when a structure is fed from a single branch circuit with a ECG does that also include a multiwire branch circuit? Wondering if that makes a difference here b/c the pole is 208.