Example: A 25KVA transformer protected by a primary 15T fuse supplys 100 Amps to an over head service for a home. The secondary is 240 Volts.
What is the interrupt rating of the primary fuse?
Is it 22,000 Amps or Greater?
Can you explain how 22,000 Amps RMS SYM interrupt rating developes in about half a cycle to open the fuse?
The Primary fuse will carry up to 150% Or 156.25 Amps. Is this the available fault current?
When a short circuit occurs in the transformer secondary.The secondary winding can carry 25KVA/240 volts or 104.166 Amps. The secondary short circuit current will pass through the transformer. But, the secondary to primary current ratio will not be high enough to open the fuse. Is this correct?
When the secondary short circuit current exceeds 104.166Amp it will blow open the winding. Is this Correct?
Is 104.166 secondary Amps my available Short circuit current can you explain?
Charlie,
Thanks for you input!
Philip
What is the interrupt rating of the primary fuse?
Is it 22,000 Amps or Greater?
Can you explain how 22,000 Amps RMS SYM interrupt rating developes in about half a cycle to open the fuse?
The Primary fuse will carry up to 150% Or 156.25 Amps. Is this the available fault current?
When a short circuit occurs in the transformer secondary.The secondary winding can carry 25KVA/240 volts or 104.166 Amps. The secondary short circuit current will pass through the transformer. But, the secondary to primary current ratio will not be high enough to open the fuse. Is this correct?
When the secondary short circuit current exceeds 104.166Amp it will blow open the winding. Is this Correct?
Is 104.166 secondary Amps my available Short circuit current can you explain?
Charlie,
Thanks for you input!
Philip