Re: Pole mounted utility transformer
sparks1:
Something is wrong here. My thinking is that when the primary of a single phase transformer like you are talking about is connected to a three phase system, there is only one voltage applied to the primary and there is only one current going through the primary, it is single phase, and you cannot talk about the two phases being 120 degrees out. And the secondary has no 120 degrees out of phase relationship either. It is a center-tapped winding. The phases are 180 degrees out of phase to each other in respect to the neutral.
BTW there is a such thing as two phase but not in this case.
edit: jim beat me to it...
[ January 26, 2005, 04:13 PM: Message edited by: crossman ]
sparks1:
Something is wrong here. My thinking is that when the primary of a single phase transformer like you are talking about is connected to a three phase system, there is only one voltage applied to the primary and there is only one current going through the primary, it is single phase, and you cannot talk about the two phases being 120 degrees out. And the secondary has no 120 degrees out of phase relationship either. It is a center-tapped winding. The phases are 180 degrees out of phase to each other in respect to the neutral.
BTW there is a such thing as two phase but not in this case.
edit: jim beat me to it...
[ January 26, 2005, 04:13 PM: Message edited by: crossman ]