Page 52 onwards, WOW! :happyyes::happyyes: BIG thanks :happyyes::happyyes:
Does not have any line to neutral loads on the secondary help in any way in both these designs?
Surges can also start on the POCO primary and appear on the transformer secondary so having no LN loads does not solve the problem.Page 52 onwards, WOW! :happyyes::happyyes: BIG thanks :happyyes::happyyes:
Does not have any line to neutral loads on the secondary help in any way in both these designs?
Surges can also start on the POCO primary and appear on the transformer secondary so having no LN loads does not solve the problem.
All of our SC meters have spark gapsOk, I was just thinking something along the lines of this, for better or for worse:
https://forums.mikeholt.com/showthread.php?t=198546&p=2000967#post2000967
All of our SC meters have spark gaps
self-contained
According to ANSI Standard 37.010 TABLE 11 -Distribution Transformers-Single-phase secondary 240/120 or 480/240 and primary from 2400/4160 up to 24940/14400 V 25 kVA Z=2.4-2.6 %.
Ignorant Scottie strikes again..............Any one have an idea what the impedance is of a typical 25kva pole top POCO transformer? A range is fine. Any chance it will be less than 1.1%?
It doesn't, but the fact it is designed to hang at the top of a pole might mean there are some differences between it and similar capacity unit not designed to hang at the top of a pole.Ignorant Scottie strikes again..............
Why would the mounting position make a difference to the impedance?
Different physical size/shape/configuration. Also, most 3-phase UG is in a single tank while OH 3-phase tends to be in separate tanks banked together.Ignorant Scottie strikes again..............
Why would the mounting position make a difference to the impedance?