giddingselectric@monmouth
Member
just built a 1200a service. have three conduit runs and put one phase in each conduit. i asked inspectors and power company if this was ok and they had no problem. i know what code says to alternate phases in each conduit because of harmonics but i was undermaned at the time and it was simpler for them. now that they hooked up permenant power meter guy says this is a melt down hazard and needs fixed asap. i just orderd 3000.00 worth of material to fix it the way they want it but it wont be in for a few days. i need to know how much of a problem this is. could somebody please tell me(other than rephrasing the code book) if they have ever experianced a problem with this. because all i am getting around here is hear say. i took a infared thermometer out there and there is only a 10 degree difference between conduit and room.