LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
With all of the stray-voltage threads we've had, I think I'd want bonding done even on a pool with no electrical equipment.
Seems i'm always the head asking theory Q's here InfinityAnd why the poop emoji?
You still have to add the EPBG even if no power to the pool. You may only be bonding the perimeter to the water but it is required.With all of the stray-voltage threads we've had, I think I'd want bonding done even on a pool with no electrical equipment.
When was this? Haven't done pools for very long.Further, there was a lot of activity when the NEC allowed pools to be part of the whole GEC scheme
~RJ~
It is on the same concept as barn or even the remote watering stations, the EPB brings everything the livestock might contact all to the same potential recognizing that there are times NEV is present and the potential gradient or differential was causing issues. In the barn situation they will create a gradient at entry points that will allow a gradual change from the unbonded surface and any voltage present on the EPBonded surface.so would the same theory apply to barns >547??
~RJ~
yah i suspect that code was written with DIYers in mindAccording to 2020 680.22(E), a panel shouldnt be within 5’ of a pool…. unless separated by a barrier.
Final inspection last week on pool. Inspector failed. Stated the Jandy sub-panel, the (4) 12V transformers and the Jandy power center for the salt system must be bonded. There are lugs on the Jandy equipment but none on the Intermatic transformers.
Pool equipment 40' from the pool.
We had bonded same equipment set up about 15 years ago, and the inspector at that time said no need to. Go figure.
I copied that section of the code Dennis referenced, 680.26 (B). Perhaps I'll show the inspector.
The power center for the salt gets it's power from the Jandy panel. I can see his argument as well.All equipment associated with the pool needs bonding. I guess an inspector can argue that the pool panel is equipment for the pool. What I have seen mostly, that is before these Jandy boxes were around or being used, was a standard panel that we used as a sub out at the pool. We drove rods and treated it like a remote subpanel.
I would agree the power center for the salt system should be bonded but not the Jandy---however I can see his argument also.
What nec year are you using?The power center for the salt gets it's power from the Jandy panel. I can see his argument as well.
He was nice enough about it. No big deal. We can make the change. He did tell me concrete pools no longer needed the water bond. Not sure about that.
(C) Pool Water.
Where none of the bonded parts are in direct connection with the pool water, the pool water shall be in direct contact with an approved corrosion-resistant conductive surface that exposes not less than 5800 mm2 (9 in.2) of surface area to the pool water at all times. The conductive surface shall be located where it is not exposed to physical damage or dislodgement during usual pool activities, and it shall be bonded in accordance with 680.26(B).
ENHANCED CONTENT
Collapse
Where bonded items such as ladders, rails, or underwater luminaires are in direct contact with the pool water and provide the required surface area, it is not necessary to provide another conductive element. A conductive pool shell in contact with the water also satisfies this requirement. However, where the pool does not include any of those items, it is necessary to install a conductive element. Devices have been specifically listed as a means to provide this contact with the pool water.
I'll still continue to use the water bond fitting. I use the 1" in line version.What I link about the NEC Link is that they explain certain sections. The enhanced contents explains things better at times. The bold shows where a conductive shell in contact with the water will satisfy the requirement for bonding the pool water. But this is the 2020 nec. I'm am not sure the 2017 hits on this- at least not clearly
Here is the section
Good point. I have never bonded the pool panel but I was curious as to why the manufacturer had a bonding lug for it. (I have heard there is a lug)680.26(B)(6) specifies electrical equipment associated with the pool water circulating system...NOT all pool equipment.
IMO...12-volt transformers 40' feet from a pool do not need to be bonded under 680.26
That is a good point in that the EPB cannot be used for a GEC.Here is the twist what if that sub panel was fed by outside feeder? NEC 2017 section 250 says equipotential grid cannot be used as grounding electrode??? You still bond it to sub panel?