Re: Pool Bonding
Don: I can't think of an appliance that will be used near the pool metal parts. So lets say the lady has her washing machine under the diving board
The washer draws 10 amps. The No.#12 run is 200 feet in length. Voltage drop is 12.6 volts.
This appears as 12.6 volts common mode voltage at the appliance.
Now consider the pool metal. This metal is connected to the earth and the MGN of the distribution system. Current will be flowing in this conductor. This current can be 180?out of sync with the appliance. The voltage difference can be elevated according to the amount of transient current in the pool system.
Now feature a flashover at the high voltage bushing on the distribution transformer. This arc will raise the voltage at the pool equipment more than at the neutral bus of the service.
I maintain the pool metal should not connect to the electrical system.
I am open to other opinions. This is only my perception.
Don: I can't think of an appliance that will be used near the pool metal parts. So lets say the lady has her washing machine under the diving board
The washer draws 10 amps. The No.#12 run is 200 feet in length. Voltage drop is 12.6 volts.
This appears as 12.6 volts common mode voltage at the appliance.
Now consider the pool metal. This metal is connected to the earth and the MGN of the distribution system. Current will be flowing in this conductor. This current can be 180?out of sync with the appliance. The voltage difference can be elevated according to the amount of transient current in the pool system.
Now feature a flashover at the high voltage bushing on the distribution transformer. This arc will raise the voltage at the pool equipment more than at the neutral bus of the service.
I maintain the pool metal should not connect to the electrical system.
I am open to other opinions. This is only my perception.