The situation I 've been asked about is --- the pool deck will have drains for shed water, the pool drain piping is to be a PVC material, the contractor has been asked to install an 240v deicing heat cable in the piping, & now the NEC does not require circuits to be pool associated outside of 5'of waters edge.
I really can't justify 680.27(C)(3) as the cables do not meet the embedded requirement/or do they?
Violation? Hazard?? or just wrong???
680.27 Specialized Pool Equipment.
(C) Deck Area Heating. The provisions of this section shall apply to all pool deck areas, including a covered pool, where electrically operated comfort heating units are installed within 6.0 m (20 ft) of the inside wall of the pool.
(3) Radiant Heating Cables Not Permitted. Radiant heating cables embedded in or below the deck shall not be permitted.
I really can't justify 680.27(C)(3) as the cables do not meet the embedded requirement/or do they?
Violation? Hazard?? or just wrong???